What is the minimum UPS wattage required for a blade enclosure that consumes 2500W and can have an additional seven blades at 200W each?

Prepare for the CompTIA Server+ Exam. Use flashcards and multiple choice questions to test your knowledge of server installation, configuration, and management. Ace your exam with comprehensive study guides and detailed explanations!

To determine the minimum UPS wattage required for the blade enclosure, we need to calculate the total power consumption based on the given data.

The blade enclosure itself consumes 2500W. If you can add seven additional blades, each consuming 200W, the additional power required will be:

7 blades x 200W per blade = 1400W

Adding this to the base power requirement of the blade enclosure:

2500W (enclosure) + 1400W (additional blades) = 3900W

When determining the minimum wattage for the UPS, it's essential to consider operating conditions and potential power spikes, which are common in data center environments. Therefore, it is prudent to select a UPS that can handle slightly more than the calculated requirement to ensure reliability and avoid overloading.

In this scenario, rounding up from 3900W leads us to the next standard UPS wattage, which is 4000W. This allows for a safety margin, preventing any performance issues under full load conditions. Thus, the minimum UPS wattage required would be best covered with a 4000W option, ensuring that all components receive adequate power and that the system operates efficiently without risking overload.